View Full Version : FISHER PRICE BREAKER?
Does anyone know if there are any requirements on what breaker to use for fisher price motors? Whether it is a 20,30, or 40 amp fuse?
I've gone through all the documentation and could not find any specifics.
At the moment, our robot has 2 wired with 14 awg wire to 30 amp breakers.
There are no restrictions. However, if you notice the FPs tripping the breaker a lot, or you're not getting expected results, go up to a 40A breaker and 12AWG wire. They can take that.
Al Skierkiewicz
17-02-2010, 17:48
TPN,
There is no restriction on what breaker to use with any motor. The breaker rules match breaker size to wire size. You can run an FP motor from a 20 amp breaker if you wish. It needs to have a #18 wire or larger if that is the breaker you choose.
<R47> All active Power Distribution Board branch circuits shall be wired with appropriately sized wire:
A. 12 AWG (2.052mm) or larger diameter wire must be used for all circuits protected by a 40A circuit breaker.
B. 14 AWG (1.628mm) or larger diameter wire must be used for all circuits protected by a 30A circuit breaker.
C. 18 AWG (1.024mm) or larger diameter wire must be used for all circuits protected by a 20A circuit breaker.
Thanks for the answers guys!
Adam.garcia
18-02-2010, 03:36
Actually today we ran into that problem. We concluded that the 30 Amp Breaker is the best and most reliable for the job.
Al Skierkiewicz
18-02-2010, 07:29
Adam,
Can you tell us how you got to that choice? Inquiring minds, you know.
vBulletin® v3.6.4, Copyright ©2000-2017, Jelsoft Enterprises Ltd.