geomapguy 11-09-2012 20:14

From 24V to 12V
 
Is there anyway to change the 24V Double Solenoids to 12V instead.

Al Skierkiewicz 11-09-2012 21:03

Re: From 24V to 12V
 
No,
The solenoid coils are optimized for 24 volts. They might operate at 12 volts but not reliably.

Camren 11-09-2012 21:24

Re: From 24V to 12V
 
Is the 24v solenoid your robot (If so I have a solution) or is it for a electronics project (if so I have another solution)

Gdeaver 11-09-2012 21:56

Re: From 24V to 12V
 
For SMC solenoids it's just a matter of swapping out the 24 volt coil for a 12 volt one. Imagine it's similar for the KOP solenoids.

IndySam 11-09-2012 22:03

Re: From 24V to 12V
 
You can buy the 12vdc sub-bases from AndyMark and convert the KOP solenoids.

They will work at 12 or 24 volts.

ratdude747 12-09-2012 14:28

Re: From 24V to 12V
 
If it is for a FRC bot I would just wire them to use 24v from the distribution board... 24V works a lot better from my experience.

jspatz1 12-09-2012 14:57

Re: From 24V to 12V
 
The solenoids are interchangable on the valve and 12v solenoids can be obtained from Festo or a dealer.

Neither 12v or 24v solenoids work better or worse than the other. The coils are designed to provide the same function, and are simply offered in different voltages to match the users needs. There could be some difference in the stabilty or capacity of the 12v or 24v supply on the robot.

Jon Stratis 12-09-2012 15:28

Re: From 24V to 12V
 
Also important to keep in mind... running one of the typical 24V solenoids on a 12V relay can drive you mad trying to debug the problem. The LED's on the solenoid can light up and make it look like it's working, but it won't actually switch anything!

jspatz1 12-09-2012 17:26

Re: From 24V to 12V
 
Quote:

Originally Posted by Jon Stratis (Post 1185299)
Also important to keep in mind... running one of the typical 24V solenoids on a 12V relay can drive you mad trying to debug the problem. The LED's on the solenoid can light up and make it look like it's working, but it won't actually switch anything!

A very common problem I have seen often, usually from teams who have followed a KOP wiring diagram using 12v breakout board.

geomapguy 13-09-2012 16:53

Re: From 24V to 12V
 
We are using it for an offseason robot project.

Camren 13-09-2012 18:08

Re: From 24V to 12V
 
Use the 24v pd slot