Pressure Switch
Right now I have a compressor continuously running. How do I add a pressure switch so it shuts off at a certain psi. This is what my code looks like so far (ignore the Digital Modules). Thanks!
Allons-y! |
Re: Pressure Switch
1 Attachment(s)
Here is my code.
|
Re: Pressure Switch
A pressure switch should be wired up to DIO 1 as your code specifies.
One wire to signal, the other wire to ground. This switch is preset to turn off around 115psi and back on at 95psi. ![]() |
Re: Pressure Switch
Quote:
|
Re: Pressure Switch
Quote:
|
Re: Pressure Switch
Quote:
|
Re: Pressure Switch
Does the pressure switch calibration need to be checked and adjusted this year? |
Re: Pressure Switch
There is no adjustment on the pressure switch.
You might be thinking of the pressure relief valve which has to be adjusted to 125psi. |
Re: Pressure Switch
Quote:
|
Re: Pressure Switch
The problem was a bad connection between the sidecar and the spike. All is well now. Thank you everyone.
|