Location of the PD Board
Referring to rule 42
Quote:
|
Re: Location of the PD Board
Quote:
|
Re: Location of the PD Board
From personal experience we have never had an issue with a clear cover over our breakers.
I think this rule exists so inspectors can look to make sure the amperage rating is correct for each motor. |
Re: Location of the PD Board
Quote:
We're looking for wire sizes and proper hookups (1 wire per Wago, radio and cRio power, etc.) along with amperages for motors and all of the other PD rules. I actually had to have one team turn their robot on its side to see the PD board; neither of us appreciated the extra time that inspection took. |
Re: Location of the PD Board
All,
The rule exists so that inspectors can be sure you have the legal breakers installed, that the breaker meets the minimum wire size for the rating and that there is only wire in each WAGO terminal. We then check to see that the radio is wired correctly as is the Crio. During Power On testing we also check to see that all LEDs are lit. We will work with you if your design requires a special mounting, access or cover, but if you make impossible to see the above conditions you will have to correct it. |