Baldwin Robotic 18-02-2013 21:35

Solenoid problems
 
hi,
our team has almost a day left before we put the robot in a box and ship it out so please answer quick.

we have programmed and wired correctly the 2 double solenoids that we are using, the lights changed from side to side (like their suppose to), and the the pneumatic pistons have pressure in them. But when we push the buttons to go down and up the pistons do not change.

please help
thanx

Garten Haeska 18-02-2013 21:40

Re: Solenoid problems
 
Do the lights on the solenoid breakout board (on the cRio) change along with the ones of the valves?

Baldwin Robotic 18-02-2013 21:48

Re: Solenoid problems
 
yes, they do change at the same time the valves do.

Mark McLeod 18-02-2013 21:57

Re: Solenoid problems
 
  1. Are the solenoid coils marked as 12v or 24v?
  2. What voltage do you have wired into the Solenoid Breakout - 12v or 24v?
  3. Is the power status light on the Solenoid Breakout bright green?
  4. Does the Solenoid Breakout have 2-pin ports or 3-pin ports?
  5. Are the red wires connected from the solenoid to the outside pin on the Solenoid Breakout, and the black wire connected to the inside pin of the connection?

Baldwin Robotic 18-02-2013 22:04

Re: Solenoid problems
 
1. they are 24v
2. they are wired 24v
3. yes it is bright green
4. it is two pin ports
5. and yes they are red out side and black inside

Baldwin Robotic 18-02-2013 22:09

Re: Solenoid problems
 
the solenoid break out is actually 12vs... ops found the problem but how do we fix that?

EricH 18-02-2013 22:24

Re: Solenoid problems
 
Quote:

Originally Posted by Baldwin Robotic (Post 1235985)
the solenoid break out is actually 12vs... ops found the problem but how do we fix that?

Someone else just asked that earlier today--use the open slots in the 24V port the cRIO connects to. I believe they're C and NC, can't quite remember which wire goes to which.

Kevin Sevcik 18-02-2013 23:38

Re: Solenoid problems
 
The PDB datasheet suggests the terminals go +-+-. Best bet is to check with a voltmeter, though.

Baldwin Robotic 19-02-2013 21:41

Re: Solenoid problems
 
Thank you for all your help!

Now it is time to put the robot in the box!

Mark McLeod 19-02-2013 21:54

Re: Solenoid problems
 
What do you mean?
We have two whole hours left.
Enough time for a redesign...:)