Re: Calibrate Pressure Switch?
Quote:
Quote:
|
Re: Calibrate Pressure Switch?
Quote:
|
Re: Calibrate Pressure Switch?
Or send it to me please. I love to break things to see how they work.
|
Re: Calibrate Pressure Switch?
Quote:
Edit: Or I can send it to AL |
Re: Calibrate Pressure Switch?
I contacted Nason today and spoke with their technical support for the SM switch. They did indicate that it comes precalibrated/preset from the factory. They did indicate that if it is out of calibration you could contact them and they would be happy to repace it or recalibrate it by giving you an RMA. The technical support rep said that if the end user wants to "tweak" the pressure, that they will not warranty it. They said to field calibrate it, but only in a small band ~5-10psi, this is what they do at the factory if the proper base was assembled. The factory uses different bases that have different height diaphram pins for different PSI ranges. I asked that if the switch setscrew is loosened and silicone is removed is this a safety issue, and they indicated that the entire plastic top (limit switch) is removable without a safety problem. We did take one appart at our shop and it is a limit swith screwed onto a blind threded hub with a small diaphram pin that extends out of the ~. 0625 hole to push on the limit swith metal lever. They did indicate that if you desire an on the fly fully adjustabe switch that the CJ switch is the way to go http://www.nasonptc.com/pdfs/Switches_Catalog.pdf page 13.
I could post images of a disassembled switch possibly tuesday when we have our next meeting. Edit- I see I posted this before seeing that Mark contacted them too, the only discrepancy is the psi vs 5 to 10 PSI. |
Re: Calibrate Pressure Switch?
For those lurking here, until directed by the Q&A, an inspector finding a pressure switch that has obviously broken the factory seal will be considered to be a modified pneumatic part. Fair enough?
|
Re: Calibrate Pressure Switch?
1 Attachment(s)
Attached is a print out from the Nason switch catalog showing a cut away of the pressure switch. The SM commonly used is the diaphragm type. This is pretty much how most mechanical pressure switch work.
|
Re: Calibrate Pressure Switch?
Quote:
|
Re: Calibrate Pressure Switch?
Quote:
|
Re: Calibrate Pressure Switch?
Quote:
|
Re: Calibrate Pressure Switch?
Agreed - consider pneumatic components sacred! Thou shall not touch thy pneumatics in a manner that changes their core use or function as intended by its creator. :D
|
Re: Calibrate Pressure Switch?
If you have an on board compressor you really don't want the compressor to shut off at a higher pressure, in fact you will be better off selecting a switch that turns the compressor on and off at lower pressures, assuming you have selected the proper stored volume.
Take a look at the compressor's specs and you'll see that the higher the pressure it is working against the lower the CFM output. Some examples 80psi .45cfm 90psi .43cfm 100psi .39cfm 110psi .36cfm 120psi .34cfm Note those numbers are based on a supply voltage of 13.8 v something that a FRC robot does not have the luxury of, and with a working voltage in the 11-12v range I would expect a steeper drop off of performance. Personally if I were to select a switch I'd choose one that turns on at ~80 psi and off by ~100 psi to minimize the refill time, the heat build up and general stress on the compressor. If you've sized your storage system properly there should never be a case where the stored pressure drops below 60 psi with a 80/100 switch. Now if you have an off board compressor there could be an advantage to selecting a switch that shuts off at 120psi but that would be minimal compared to the commonly used 115psi switch. Either way a switch that has its calibration screw fixed in one way or another by the mfg should not be adjusted, doing so would be considered tampering with or modifying a pneumatic component and make it illegal. |
Re: Calibrate Pressure Switch?
Quote:
![]() ![]() ![]() ![]() |
Re: Calibrate Pressure Switch?
Mark et al,
It is pretty obvious now that you have posted the pictures. The switch is using a standard snap action microswitch. These are not precision devices (the switch) and one must position the switch at a point where the lever will move enough to change the switch state. The hysteresis naturally occurs in the snap action mechanism of the switch. As the catalog page shows, the plunger moves when a specific pressure is reached or exceeded. It does not move a distance that is proportional for pressure. Mark, you can verify this action by applying pressure to the now open switch. I bet when it reaches ~120 psi, the plunger will suddenly move out. |
Re: Calibrate Pressure Switch?
Can pressure switch be replaced with this pressure sensor and then calibrate within the code?
http://www.digikey.com/product-searc...ds=734-1003-ND |