RyanCahoon 06-02-2014 16:13

Shared Ground Connection for Pneumatic Solenoid Valves
 
Would there be any issues (ground loop, etc) with running pneumatic control lines (from the NI 9472) with a shared ground connection? I'm trying to reduce the number of wire runs to our manipulator, and hoping it wouldn't be a problem because they're relatively low-power digital signals.

Thanks,

apalrd 06-02-2014 16:23

Re: Shared Ground Connection for Pneumatic Solenoid Valves
 
On the blue solenoid breakout board, if you look carefully (or look at the schematic), the ground pins all go to the ground plane anyway, so it's kinda irrelevant electrically.

Al Skierkiewicz 07-02-2014 07:52

Re: Shared Ground Connection for Pneumatic Solenoid Valves
 
Ryan,
There is no rule against that. However, good electrical practice recommends that the single return wire be a larger gauge than a single valve. If you are running more than two valves, I would recommend a #18 or larger for this wire.

RyanCahoon 09-02-2014 23:18

Re: Shared Ground Connection for Pneumatic Solenoid Valves
 
Al and Palardy,
Thanks for the information and advice.