Re: Air Compressor not turning off.
Quote:
Right now we will try a new PCM and see what happens. We will try this tomorrow. I will keep you updated. |
Re: Air Compressor not turning off.
Quote:
|
Re: Air Compressor not turning off.
Quote:
The compressor STILL is not turning off -- while minutes before, the other (v1.6) PCM was working perfectly. Also, after removing the 2 pressure switch leads from the PCM, we see this: The self test completed successfully. PCM is enabled. Compressor is close-looped on sensor Comp Is On Pressure is not full Checked also for damage, shorts, or stray wire bits, but it's clean. Other than getting another PCM to try, I don't know what to do next. Ideas? |
Re: Air Compressor not turning off.
So judging from the Self-Test the PCM reports that the "Pressure is not full" despite the pressure-switch inputs on the PCM not being wired to anything. That is likely the root cause for WDB's symptom, and not firmware. This sounds like hardware and your "other PCM" likely works regardless of what firm is in it.
To further confirm it's not a firm issue, I put up 1.60 PCM firm (one-dot-sixty) at... http://www.crosstheroadelectronics.c...ation-1.60.crf ... Flash 1.60 back into your bad PCM and I bet you will still find that the self-test still reads "Pressure is not full" despite having the PCM not connected to the pressure-switch. For any given functional PCM : When the pressure switch is not connected, Pressure should read as "Pressure is Full", regardless of all other factors. This is deliberate so an unplugged pressure switch causes compressor to stop. dumbuya, can you do the same check? Unplug the pressure-switch from the PCM and run the Self-Test to see if the pressure still reads "Pressure is not full". At any rate dumbuya and WDB, I recommend contacting support@crosstheroadelectronics.com for next steps. |
Re: Air Compressor not turning off.
1 Attachment(s)
Quote:
Confirmed. Reflashed the suspect PCM back to 1.6 and the same behavior was observed. Removing the pressure switch from the PCM should not allow the compressor to run, but it still runs. So it looks like a hardware problem with this specific PCM. Put in our other PCM in and it works perfectly. We took a picture of the board near the pressure switch contacts and there might be some anomaly there (you'll have to zoom in a little), but we'll get a replacement PCM anyway. Thanks Omar for your assistance! |
Re: Air Compressor not turning off.
Quote:
However, I cannot tell you what we find to be the issue other than to say we might have had bad PCM. One thing I could try is update 1.6 firmware in the old ( "bad") one and see if it is going to respond as intended. Thanks for your urgent response to the issue. |
Re: Air Compressor not turning off.
Thank you to all for sharing your experiences with the PCM.
We swapped the PCM with a new one and it worked as expected. |