![]() |
Re: Al's Annual Inspection Thread 2015
It's not an unusual issue, even for experienced teams.
I was inspecting the wiring from our CIM motors back to the speed controllers, and asked whether they had looked at the wiring table. Turns out they matched the wire off of the CIMs, rather than using the table. Fixing it is now on our punch list. |
Re: Al's Annual Inspection Thread 2015
Another pneumatic system question: does the steel NPT fitting, standard on the Viair compressors, need to be installed?
It is the compressor's fitting that typically comes with a plastic plug in it, seen here: ![]() |
Re: Al's Annual Inspection Thread 2015
Quote:
The pressure relief valve must be attached to the compressor with legal hard (non tube) fittings, so if you chose to install the NPT to plastic plug fitting, it must be past the pressure relief valve. Quote:
|
Re: Al's Annual Inspection Thread 2015
Quote:
Why don't you want it? It doesn't add much weight, and it gives you an easy adaptation to a tee fitting for the relief valve. |
Re: Al's Annual Inspection Thread 2015
Quote:
|
Re: Al's Annual Inspection Thread 2015
Quote:
Quote:
The steel coupler pushes a few fittings and a gauge to a spot that's less accessible (and makes the gauge less readable) so it is handy to not have it in place. The port in the compressor is 1/8NPT, so attaching normal hard-fittings and tees is the same as attaching to the steel part, it just fits into our robot a bit more easily. |
Re: Al's Annual Inspection Thread 2015
Quote:
How does it make sense that I would have to crimp 12 AWG wire to 14 AWG wire after the speed controller to be legal? How does that help? |
Re: Al's Annual Inspection Thread 2015
Quote:
R65 C might give you a little leeway with that idea though since you are using the existing threads. |
Re: Al's Annual Inspection Thread 2015
Quote:
R65-C is why I assume our actions are legal, but I just want to double-check with the in-field experts. |
Re: Al's Annual Inspection Thread 2015
Quote:
|
Re: Al's Annual Inspection Thread 2015
Quote:
Quote:
|
Re: Al's Annual Inspection Thread 2015
Quote:
Now, if it came with it installed, then the question is whether R65-C applies since you would be "disassembling" to remove the NPT fitting, and not "assembling". |
Re: Al's Annual Inspection Thread 2015
Quote:
FIRST doesn't want you replacing wires that were not intended to be replaced. Thus the concession granting exception to using wire as supplied by the manufacturer. |
Re: Al's Annual Inspection Thread 2015
Quote:
|
Re: Al's Annual Inspection Thread 2015
Quote:
PDB <-> 40A Breaker <-> 12AWG wire <-> Victor <-> 14AWG wire directly attached to CIM Legal? |
| All times are GMT -5. The time now is 15:27. |
Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi