Autonomous chooser not working when connected to the field
We spent the day yesterday trying to figure why when tethered out autonomous chooser worked but wirelessly on the field the bot sat dead in autonomous. We worked with a few techs and found that turning off the windows fire wall worked. We had 7 qualifying rounds today and the last one we had no autonomous again. Brought it back to the pits, tethered and worked. ANY ideas? We have one more qualifying match tomorrow before finnals. We are currently sitting in 19th with strong possibility of making to a final alience.
|
Re: Autonomous chooser not working when connected to the field
Do you have a connection indicator on the dashboard? What did it say? Are you using the LabView dashboard or the Java/C++/Python etc one?
What I would do in your position is add a connection indicator on the dashboard. This will tell you whether the dashboard can connect to the NetworkTables server. If the SD isn't connecting very soon after the robot is connected, reboot the roboRIO. We had this same problem occur in a practice match, but not since. No guarantee of this working, but I've had trouble with the roboRIO not fully booting up a few times today. If I have a chance, I'll come over tomorrow morning to try and help some more. |
Re: Autonomous chooser not working when connected to the field
Quote:
|
Re: Autonomous chooser not working when connected to the field
If you do have a connection indicator and it was green and your selected autonomous still did not run, select a different autonomous mode and then re-select your desired autonomous. You may have a race condition where your selected autonomous doesn't get sent over to the robot initially.
|
Re: Autonomous chooser not working when connected to the field
We do have a connection indicator but will have to ask the drive coach and team if they noticed the status. Most likely they did not . The select / reselect was a rouble shooting step attempted yesterday but since today the entire day it was running flawlessly the drivers hadn't been doing this. We also started yesterday with static IP's but after our radio flash that didn't work. The IP was 10.32.44.5 that I believe now was wrong. Should been like 10.32.44.20. Our ip camera is static with an ip of 10.32.44.11 and is lagging but displayed on the SD.
nickbrickmaster love to pick your brain for my own knowledge. You must be here at 10,000 lakes. We have a slow start in the morning. Our first and final quality is at 11:30 ish. Our plan is to re-weigh since we beefed-up a part of our bot with about 12oz and with a 119 lbs bot yep it must be done. |
Re: Autonomous chooser not working when connected to the field
Quote:
|
Re: Autonomous chooser not working when connected to the field
Thinking about adding the line
Code:
public void autonomousIntit () { |
Re: Autonomous chooser not working when connected to the field
If selections aren't showing up on your dashboard, restart the robot program. The dashboard relies on the initial sending of selections on program start to know what they are.
Also, as other people have said, sometimes selectors are picky. What we did was print out what the robot thought was selected in disabledInit() so we could check if we needed to reselect something. |
Re: Autonomous chooser not working when connected to the field
Quote:
Having said that, I believe your way would work as well. |
We also had this happen to us. It turns our that Windows 10 had re-enable the firewall. Very annoying but at least we know to look for that now. Also we ended up setting it to use static ip addresses as suggested by the FTAA. One of our eliminations alliance partners also saw the same problem... they had no firewall issue but fixed it by restarting their robot and driverstation to force a cleanup of the network tables.
|
Re: Autonomous chooser not working when connected to the field
We've had issues with GetSelected() returning null intermittently in AutonomousInit() (in C++, but it's possible that similar ones could pop up when using Java). Calling GetSelected() in DisabledPeriodic() instead and storing its return value has been somewhat more reliable.
|
Re: Autonomous chooser not working when connected to the field
We endd up with this
Code:
public void autonomousIntit () {http://www.chiefdelphi.com/forums/sh...d.php?t=141684 Code: System.out.println("Hello From the Rio"); //Print to RioLog Just a tool this team has not ever used and I need to get and get them used to using. I'm learning and introducing the team to command based programming and more advanced controls. Thanks for you help and suggestions. With a 15 place qualify and a 7th alliance second pick we help the quarterfinals go three rounds with a close game #2 and #3. If our auto worked could had change the game |
Re: Autonomous chooser not working when connected to the field
Sorry to hear you were having so much trouble, hope that it is resolved for tomorrow.
This won't help you for this year, and I may sound like I am harping on this, but my team chose to use a hardware selector switch instead of relying on SmartDashboard or other software solutions, for precisely this reason. The drive team appreciated having physical feedback to know exactly what the robot would do. An option to consider for the future. |
Re: Autonomous chooser not working when connected to the field
Quote:
Code:
autonomousCommand = new Auto_02_underLowbarScoreLowGoal(); |
Re: Autonomous chooser not working when connected to the field
We code in Java on the robot, and Java on the driver's station.
We've had a LOT of problems using custom network code in the last 2 years. This year we did something way different than last year - we setup a web server on port 443 of the driver's station. We could never get it working. This weekend we let the FTA's have complete logs of our stuff in the hope that someone who understands the network architecture can figure out what was going on. The firewall was disabled in every way Windows can disable the firewall. In the end, we swapped to NetworkTables. Sure, it requires a Labview runtime library just to develop with, we can't figure out how to get it above 4hz, and it means that without layers of interpreters we'll only ever develop displays in Java - but it works. We run a separate process from the driver's station, so it isn't Smart Dashboard stuff - just read and write to a HashMap by using the NetworkTables framework in your own code. |
Re: Autonomous chooser not working when connected to the field
Quote:
Here's the link they were using but I think you did the static steps right https://wpilib.screenstepslive.com/s...g-at-the-event |
Re: Autonomous chooser not working when connected to the field
Quote:
|
Re: Autonomous chooser not working when connected to the field
Quote:
Quote:
Quote:
Quote:
Both teams had issues with connecting to the robot during their first events, but after switching all devices to static IPs (robot: 10.xx.xx.2, ds: 10.xx.xx.5), we had zero connection issues. |
Re: Autonomous chooser not working when connected to the field
Quote:
The dropdowns in the stock dashboards have caused all sorts of headaches this year. |
Re: Autonomous chooser not working when connected to the field
Quote:
No one on my team uses Python, for better or worse. We have plenty of kids who eventually use it during Cyber stuff, but for FRC stuff we stick to either Java or (eventually) Web. I don't want to get into a language debate - it's just what our team knows and does. I'll check out the links you provided though. Thanks for the correction on ntcore - some of my info is 2nd-hand since I'm not on the programming team. I took a look at a few things, but it'll take a bit more analysis to figure out where it puts the rate limitation in. If not, maybe next year we'll do something like Pete Lawrey's OpenHFT and then dump the results to the web server. |
Re: Autonomous chooser not working when connected to the field
Quote:
Quote:
The nice thing about pynetworktables2js is that although underneath the hood it uses python, to use it to create a dashboard you really only need to know HTML/JS and how to run a python script. However, it sounds like it isn't really what you're looking for either, as you wouldn't be able to write anything to disk without writing some python code. |
Re: Autonomous chooser not working when connected to the field
Quote:
|
Re: Autonomous chooser not working when connected to the field
Very cool if you can help us solve this. It was a common way to execute a few different things, and write all of the data to disk on the driver's station.
Here are the streams of data through the architecture. Note - Node.js also splits off a MongoDB write of the data it receives:
I'm not sure if everything is pub/sub, or if some things just poll the node server for the 'latest' data when it is needed. I do know that they had all three of these working at the school and in the pits, but not on the field since the RoboRIO could never get to the Node server on the laptop. We had re-try logic in the RoboRIO, Node.js hardening for sudden stop/starts of connections, CORS, etc. We took the system through the flow of
I don't remember for sure if the exception on the RoboRIO side was "Connection Refused" or one of the other socket/network-related errors. I can ask though. FWIW, total network bandwidth using a 15hz update rate on telemetry and a 30fps rate on the camera (320x240) was about 3.5Mbps. |
Re: Autonomous chooser not working when connected to the field
That sounds like a reasonable flow of operations... If everything was a static IP, that should work... I bet they're blocking outbound connections on 443. Did you try different ports instead of 443?
Also, I misread what you said earlier, I read "4k hz" instead of "4hz". You should be able to get at least 10hz out of ntcore, and 20hz out of pynetworktables. I haven't really benchmarked either of them recently, sounds like something someone could do. |
Re: Autonomous chooser not working when connected to the field
We also had issues with SmartDashboard during our time at the MAR Bridgewater-Raritan event. Our SmartDashboard just would not connect to the field and the match had to be played without our autonomous. From what I remember it wasn't just us either.
We decided that we didn't want to rely on SmartDashboard, so we switched to a wheel selector (Don't actually know what is called, will find out tomorrow). We wired it to three DIO ports and using binary we select our auto. That way when we set up the robot we just move the wheel to the right number and don't have to worry about it. |
Re: Autonomous chooser not working when connected to the field
Quote:
I added a benchmark script to the pynetworktables samples, it should be pretty trivial for someone to port it over to Java/C++ et al. In it's default configuration, I got around ~19hz running on localhost. I expect that my methodology isn't perfect, but that number is around what I would expect, and varying the write flush period also varied the latency. I would expect a similar test of ntcore in its default configuration to be around 9-10hz. This doesn't reflect an 'actual' performance difference between pynetworktables and ntcore, but rather just a different default value for the update rate (I chose 50ms, they use 100ms). |
Re: Autonomous chooser not working when connected to the field
Quote:
Around this time last week someone on the programming team said they clocked Network Tables at 4hz - it matters at the moment since that's how vision sends parameters back to the robot. I'll examine how they benchmarked in more detail then. 10Hz is more palatable for post-match analysis, but in the shop I'd like to bump it higher so we can track some of the sensor outputs better. Thad, I'll look for the rate to remove it. Thanks for the tip! |
Re: Autonomous chooser not working when connected to the field
Does the ntcore implementation have a flush command? This is a good way to keep a relatively low rate of transmission, but ensure that when you want lower latency, you can do so.
And just to confirm what was said earlier, there have always been different, but compatible network table implementations. Unless you are using the LV implementation, you do not need the LV runtime engine. The Java and C++ ones are now a common implementation. Greg McKaskle |
Re: Autonomous chooser not working when connected to the field
Quote:
|
Re: Autonomous chooser not working when connected to the field
We are a labview team, and years ago we had issues with making selections on the dashboard, make it to the bot, for auto selections. The fix we implemented back then, and still use today, is that we use joysticks to make the selections, and the dashboard only displays the value. We put the code for the auto select in the disabled state. This forces communication path to the bot be working, for the selection to work.
Like I said we are Labview, but thought that this maybe a simple workaround to make sure the robot is going to run the right code. |
Re: Autonomous chooser not working when connected to the field
One thing to remember when setting static IPs that I didn't see in the thread is that the subnet mask is 255.0.0.0 and not 255.255.255.0 that you may be used to using elsewhere. This is classful addressing where the 10.0.0.0/8 RFC1918 network is being used.
|
Re: Autonomous chooser not working when connected to the field
Sorry to hear you've been having issues. We had a couple mysterious, non-reproducible issues. We've taken the following mitigation tasks:
1) Poll Smartdashboard (via getSelected()) every half-second during DisabledPeriodic() 2) Write the present auto mode number seen on the robot back to a different indicator on Smartdashboard (which provides feedback that the robot has received changes in mode) 3) Drive team actively selects a new mode every robot boot, and double checks that it's acknowledged. No OK until we confirm correct auto is going to be executed. Restart Smartdashboard or reboot robot if needed. It's held up well enough for two regional so far.... |
Re: Autonomous chooser not working when connected to the field
Quote:
We now use a python->js gateway and our web app talks to a local server running on the laptop, which in turn talks networktables to the robot. It seems reliable. We also do some of the things mentioned in this thread like echoing the selected auto mode to another control and showing a robot generated timestamp to validate connectivity. |
Re: Autonomous chooser not working when connected to the field
Quote:
I really wanted to be able to leverage object serialization so I continued on the road you guys started down. We were able to side step a lot of the FMS network issues by taking slightly different approach on the general network architecture. We have an onboard laptop that actually runs the server and acts as the middle man. That way the FMS doesn't interfere with communications between the Rio and the Auto Manager. Basically when a socket is opened we send the latest selected auto, so just declare the auto while you're in queue and you're should be good to go. If the drive team needs to, they can change the auto from the DS via a web dashboard, and the server can broker the change to the Rio. As you suggested though, this can often be a headache because of the FMS wifi setup. We actually leverage this same general architecture for generating trajectories on the fly and for vision processing as well. Being able to use Jackson or Gson for object serialization makes life sweet when programming in Java. It made re purposing the general idea for multiple purposes fairly straightforward. |
Re: Autonomous chooser not working when connected to the field
Quote:
|
Re: Autonomous chooser not working when connected to the field
Regarding Flush:
I put flush in the LV implementation from the beginning so that camera code results or other potentially time sensitive values could have minimal latency. Rather than a write through where you are more likely to have inconsistent values, I chose to simply goose the timer and transmit all pending updates immediately instead of waiting for up to 99ms to transmit. I didn't limit how often they could call flush and I'm not aware of an issue caused by it. As you mentioned, most values are updated at 50Hz, and that isn't much bigger than 10Hz. So if a user flushed each teleOp, they have only affected bandwidth by 5x at most. Also, only modified values are transmitted. I also allowed the user to specify how often their client or server waits to transmit updates. It defaults to 100ms and I haven't really heard of anyone using other values. For most NT stuff, 10Hz is fine. By the way, the auto chooser for LV has its own rough edges. I'll document them here. The selector presents all strings written to it within Begin.vi. Sometimes users don't find that initialization spot. On selection, it writes the selection to the robot. But if the robot writes the value, it doesn't update the dashboard selector. If the user builds a custom dashboard, they can change the default value of the selector, but the network table value isn't transmitted until it is changed. They would want to write the variable once anyway. Hope to make it smoother next year. Greg McKaskle |
Re: Autonomous chooser not working when connected to the field
Quote:
In our case match one ran as expected but some time during the match the pinball Choo choo was hit and the escapement jammed. Our Auto sequence is this: 1 Reset pinball if not on switch 2 open claw 3 close claw 4 lower wrist 5 drive under low bar 6 spin 90 deg 7 strafe to castle wall and raise wrist to fire angle 8 fire ball Match 2 we observed the ball was never fired but it must had released and the cam came off the reset switch. (no step 8) In the tie breaker step one never finished because it was jammed (observed in the pits when our tears finally dried). The turnaround time is so fast during elims there was no reset/test time in the pits. We further proved this theory by looking at the driver station log files and observed the PDP currents for the Pinball, claw and wrist. In match one the pinball was already set on step 1 so no current resisted till step 8 on that channel. In match 2 the pinball fired but is hard to tell if it rest In match 3 we see when Autonomous starts the pinball channel goes high current, looks to trip the breaker, rest and autonomous is over. If you have not ever look at these log fills ( I never have) do so look at a normal match, look at a match that did not go so well. I now know to plan if a command does not Finnish in a reasonable time it maybe best to time out and move on. Code:
addSequential ( new my_Command , timeout) |