Can I branch the CAN to go to two separate places?
So far, we've always been wiring CAN devices in series so that one pair of CAN wires on a device feeds directly into a pair on the next device, and all devices are in series. What would happen if I were to branch the CAN so that the output wires on a device split and I sent the two resultant pairs to different devices? I've read technical documentation on the CAN so I have some ideas, but I'd like to get an opinion from someone who knows about this in detail before I draw a (potentially incorrect) conclusion.
|
Re: Can I branch the CAN to go to two separate places?
If you get it Phased correctly it should work. Do you have the access to just try it? I am curios to find out.
|
Re: Can I branch the CAN to go to two separate places?
It's not recommended but I've seen teams do it and not have any issues. It's probably one of those things where it may work, but it may also cause problems. If you start seeing anything strange like devices not responding it would be a good place to start troubleshooting.
The CAN network seems pretty resilient, I've seen teams run with out any termination in the line. We've used a variety of interconnects between nodes without any issues, etc. |
Re: Can I branch the CAN to go to two separate places?
Yes, we're planning to try it and see how it goes. My main concerns are that it is either not legal (and by extension we would fail inspection) or not functional (the protocol depends on it being sequential and would not function correctly without it). Am I correct that I would theoretically need to add a 120-ohm termination resistor to whichever end doesn't ultimately end up in the PDP? And what do you mean by "phased correctly"?
|
Re: Can I branch the CAN to go to two separate places?
My advice would just be to not do that. I get that you might have one talon on one end of your bot, and another talon on the other end. But can wire is so thin anyway, just run a really long strip. No point in introducing points of failure into an already relatively "fragile" system.
|
Re: Can I branch the CAN to go to two separate places?
When you split a terminated bus like this you create the probability of reflections. If you look up a tool called TDR:
https://en.wikipedia.org/wiki/Time-domain_reflectometer It is not recommended to do this. Certain patterns of communication traffic might become garbled. Resulting in intermittent errors you can't see a cause for. Leaving an end unterminated is actually worse, as well would be using the wrong value terminators. |
Re: Can I branch the CAN to go to two separate places?
Quote:
|
Re: Can I branch the CAN to go to two separate places?
Early in the season, we tried using a central distribution panel for our SRXs in order to decrease the chance of cascading failures. Although this should work since CAN is wired in parallel, we had many problems especially since we were using "PWM" connectors to each one. We then switched to a soldered chain and had fewer problems.
|
Re: Can I branch the CAN to go to two separate places?
Quote:
Generally RF rules apply if you're at high frequency (such as CAN, ethernet, or Wifi/Bluetooth) or you're over a massively long distance (such as a 10 mile power transmission line). TLDR: Don't branch CAN wires, while it seems like it will work in reality it's asking for trouble. |
Re: Can I branch the CAN to go to two separate places?
If the entire collection of CAN devices and wiring is physically small enough, you can get away with just about any topology without it breaking.
My advice: don't tempt fate. Use the system as specified and as designed, with a single "chain" of devices each having their own internal very short tap on the bus. Troubleshooting will be much more straightforward. |
Re: Can I branch the CAN to go to two separate places?
Quote:
For the record, CAN is "wired in parallel" if and only if you regard the conductors as ideal. The real world scenario has imperfections like resistance, inductance, and capacitance, that make for a much more complicated electrical reality than "wired in parallel". Particularly at 1Mb/s, those lumped elements and the aforemnetioned reflection problem mean that the CAN topology is best implemented as a terminated bus with short branches. The PWM connectors are not the issue, and many teams use that style of connector in a canonical implementation of CAN with no issue. Go back to the Jaguar and the CAN bus uses RJ style connectors with no issues if the connectors are properly assembled and inserted. Connectors in CAN are perfectly acceptable, it's the network topology that needs to be respected. In other words, like Alan and others have said, don't tempt fate. Wire CAN as recommended in the documentation for best results. |
Re: Can I branch the CAN to go to two separate places?
The CAN standards allow "star" configurations for low data rates over long distances. For your peace of mind, it is probably best to avoid using the star configuration if it can be avoided. With the (low) quality of the wiring I have seen in many FRC robots, a bad connection is at least as likely to be the real cause of their CAN Bus problems.
It is the high edge-rate (short rise-time and fall-time) of the signal that directly leads to reflections, not the data rate. Of course, as the data rate rises, faster edge-rates are required to maintain signal integrity. Many of the CAN transceiver chips have the ability to reduce the edge-rate to minimize reflections when running at lower data rates. Without looking at CTRE and NI's schematics, it is difficult to know if they are using such a feature. The length of the various line lengths determines whether a reflection causes interference or not. With the rule-of-thumb signal propagation delay of 2 nsec/foot, your CAN wiring would have to be pretty long (in the order of 100 ft.) for it to have an effect on a 1 Mbps signal, longer than one could reasonably put on an FRC robot. If one wires the CAN Bus with the PDP "at the end of the chain" then one should always have the terminations. With a star configuration (or multi-star), the PDP should still be the furthest from the RoboRio. Quote:
|
Re: Can I branch the CAN to go to two separate places?
Do NOT do this! Your goal is to make the robot as robust as possible. One way to make the robot more robust is to wire the power, sensors and control lines per the recommendations of the relevant standards committees or OEMs. Use the correct tools and the correct techniques then test everything over and over again.
Could you get lucky? Sure Is it worth it? No, a hundred times no Is it a "professional" thing to do? No buyer would sign off and pay you for something wired incorrectly. You might be thinking "if it works then who cares"? This is where engineering ethics comes in - you are not compliant and you know it. So fix it! That is my two cents. I've delivered many dozens of high performance systems. And I've been on the receiving end of non-compliant subsystems and made them fix everything (using their own money). |
Re: Can I branch the CAN to go to two separate places?
Quote:
So for CANbus the sources have a particular output impedance that performs best when the load has a matching impedance (same resistance and opposite reactance). To keep things simple use wire much like the green/yellow that comes with the Talons. Use connectors with cross sections close to the cross section of the wire. Wire things in series from source to load (like CTE recommends and the CANbus standards dictate). Use a 100-ish ohm resistor for the load (termination). To do otherwise is to ask for troubles that are very difficult to diagnose. |
Re: Can I branch the CAN to go to two separate places?
Quote:
|
Re: Can I branch the CAN to go to two separate places?
Quote:
The so-called "normal" rules are really a number of simplifications and assumptions that apply at DC that don't apply when there is change in the signal. Even the complex impedance is a simplification that applies to lumped element models. Fundamentally, both of these are case specific subsets/simplifications of Maxwell's Equations, which are the set of laws that govern electromagnetism at non-relativistic conditions. I say this because I think it further illustrates the bad thinking I highlighted earlier: one must acknowledge the assumptions that are used (like assuming conductors are ideal) before applying a concept. It's one thing to use a suitable simplification because a set of conditions are met. I don't think any engineering would happen if we needed to do vector calculus when determining a load instead of using V=IR. But, as a good engineer, you need to know when you can simplify the model and when you cannot. As an aside, @ratdude: even Kirchhoff's Laws don't always apply, particularly if a changing magnetic flux is present. |
Re: Can I branch the CAN to go to two separate places?
Quote:
|
Re: Can I branch the CAN to go to two separate places?
Quote:
What do you mean by "slow the bus down"? Do you mean a slower data-rate or do you mean a slower edge-rate? |
Re: Can I branch the CAN to go to two separate places?
Quote:
Quote:
Quote:
Otherwise, obviously I agree. |
Re: Can I branch the CAN to go to two separate places?
Quote:
Quote:
|
Re: Can I branch the CAN to go to two separate places?
Quote:
Since CAN signals are NRZ digital (with the 1&0 voltages dependent on the PHY layer design) they represent a typical digital square wave of odd-integer harmonics with differential signal. The issue, and the TDR neatly demonstrates this concept, is that an analysis over time (not at any given instant) can produce reflections when the termination or legs (even the legs of the circuit inside the devices) get too long. So it's not merely the real component of the terminator resistance at work. It's the capacitance, inductance and impedance of the circuit as a whole. (Active AC components tend to introduce mathematical imaginary or polar numbers into circuit analysis so when I say real resistance I mean DC resistance.) Long story short - I don't think anyone in the last few posts disagrees that students shouldn't follow the guidelines. No one wants to have intermittent phantom problems that only happen when a certain pattern of traffic is sent over that CAN bus. I don't think I've ever seen a FRC team test their CAN bus with a BERD/BERT even though the speed is pretty high on that circuit (a T1 digital telephone circuit is basically 1.544Mbps and these are usually tested with something like a T-BERD). There's limited rational reason in the last few years of robots that the CAN bus configuration as recommended can't be achieved. Even if you somehow put a Talon 14 feet up an end-effector you could avoid doubling back with the CAN buss wire (which given you'd be running the power up there seems sort of strange) by simply ending the buss up there. There are some good examples of why a star configuration has advantages if you suspect your devices might fail to be connected. However, like in computer networking, how far does one want to go to get a star network without the circuit implications? Active CAN hubs? How about a CAN switch? (NOTE: I am making no suggesting the 2 links I provided are FRC legal or even recommended, just pointing out that such devices exist with evidence.) |
Re: Can I branch the CAN to go to two separate places?
Quote:
Related notes, from discussions with CTRE and beta testing the CAN BUS is fixed at 1Mbps (raw rate, not payload) and will not auto negotiate down. I don't think this has changed since then. Related note if I'm understanding the CAN spec correctly, if a star configuration is used, the termination resistor values need to change so the effective resistance is still ~100 ohms. This would be interesting in conjunction with the fixed values inside the roboRIO & PDP. |
Re: Can I branch the CAN to go to two separate places?
Quote:
Most of the CAN transceiver chips, like the ones I am using at work, are rated by their manufacturers for operation up to a maximum data-rate of 1 Mbps but that does not mean the system they are installed in are running at that data-rate. Data-rate is a measure (bits per second) of the instantaneous rate at which the data is transmitted over the bus, when there is data. One can also measure the average data-rate taking into account the time when the bus is inactive (unused) and any error correction made necessary due to noise or other problems (resending of packets). Edge-rate is a measure (volts per microsecond) of how fast the high-to-low and low-to-high state transitions take place. It is the high frequency energy contained in fast transitions that causes reflections. It is possible to have a CAN bus system with a low data-rate (say 1 bit per second) that has significant reflections because there are impedance mismatches AND the edge-rate is very high (the parts I am using have a spec of 35 nsec. minimum). Once a CAN Bus system is assembled, the line lengths, actual line characteristic impedances, actual termination resistance values, impedance mismatches and actual edge-rates are what determine what the peak voltage and the duration of the reflections will be. The characteristics of the reflections will generally remain constant unless the system is changed in some way. The CAN Bus receivers are connected to a circuit (usually incorporated in the microprocessor) that roughly synchronizes with the bit edges. The state of each bit is sampled in the middle of the bit period, often multiple times. As long as the reflections after a bit transition has died down by the middle of the bit period, the detected state of the bit will be accurate. This technique was developed a long time ago to make it easier for communication systems like CAN Bus to minimize the effects of reflections in the system. Many of the CAN transceiver chips can be set to produce lower edge-rates, often using an external resistor. This allows the system/circuit designer to reduce the energy in the reflections (and hence their peak voltage and duration) in the system based on his/her knowledge of the length of the transmission lines (bus length), the amount of impedance mismatch expected and the maximum data-rate required. The long and the short of it is that the CAN Bus standards were set up with the ability to tolerate some amount of reflections since the people developing the standards understood that the world is not perfect and that the systems will not be manufactured and installed perfectly. Therefore, while it is best to avoid using the star configuration since it is non-ideal, it is not "certain death" to use a star configuration or to add a branch as long as one is taking some simple precautions. Because of the inherent robustness, CAN Bus systems have found many applications outside of the original intended use in cars. |
Re: Can I branch the CAN to go to two separate places?
Quote:
Quote:
Quote:
Quote:
Quote:
Quote:
|
Re: Can I branch the CAN to go to two separate places?
Quote:
Quote:
Quote:
Quote:
For an example, consider a branch on a CAN Bus that is 10 ft long to reach a Talon SRX that is mounted on some arm on the robot using the same wire as the rest of the system. With a 1 Mbps data-rate, the bit time is 1000 nsec. With a rule of thumb value for the propagation time for a pulse down the transmission line of 2 nsec/ft, a 10 ft long branch would cause a reflection that returns in 40 nsec. after the bit transition that caused it. Assuming that the proper termination resistances at the RoboRio and the PDP are in place, it is reasonable to expect that the amplitude of the reflections would have diminished to become insignificant by the middle of the bit time, 500 nsec. after the bit transition. Based on the calculation shown above, I would determine that the risk of using the 10 ft long branch is minimal. Since each person/team is willing to accept different levels of risk, I can understand if you choose not to use such a branch. |
Re: Can I branch the CAN to go to two separate places?
Quote:
|
Re: Can I branch the CAN to go to two separate places?
As I am a CSA: I usually make my recommendations and explain that the default recommended configuration includes ample consideration of system traits, that a star configuration adds risk.
If a team proceeds, has issues, and refuses to change course there is nothing I can do than to keep suggesting that using the branches/star puts additional potential for issues into that system. Sure if all the connections are great the reflection shouldn't be an issue, but then again if those CAN bus wires are moving around... With the telephone style Jaguar CAN/serial connectors and a Jaguar say 15 feet away on an end-effector are you really sure the connector will not move at all so you can predict the characteristic of that network? Maybe on a bench test this would be okay but what about when that extended end-effector gets smacked by another robot? |
Re: Can I branch the CAN to go to two separate places?
Quote:
Quote:
I may have overlooked them but I don't recall seeing strict limits on the wire size and the twists per foot for the CAN Bus wires to make the characteristic impedance of the wiring more uniform in any documentation from NI, CTRE or any other FRC related sources. I also don't recall seeing requirements for shielding of the CAN Bus wires. There is no requirement that the termination resistors are high accuracy types. Those are the sorts of things one would have to do to make the CAN Bus characteristics more stable but doing those things probably takes one past the point of diminishing returns and greater/unnecessary cost/effort. With regard to risk management, please keep in mind that the size of the CAN Bus network in an FRC robot is a small fraction of the maximum size intended in the standard. Digital communication systems like the CAN Bus are developed with significant noise margins to guarantee successful implementations by relatively unskilled installers. That is where the restrictions such as the maximum length of the bus come from. As long as one is only using a fraction of the noise margin that has been built into the technology, one should be pretty certain of success. Looking at the big picture, by following some fairly simple recommendations, the risk of the CAN Bus being the cause of a failure on the field is significantly less than other sources of risk such as choosing the wrong sort of drive train or scoring mechanism. |
Re: Can I branch the CAN to go to two separate places?
Quote:
I am not being overly critical of the Jaguar, but FRC11 finally decided to stop fielding them and they now are in a box in my one shop as a result. They were too complex to debug in the 6 week season, changed manufacturer too many times to get fixes and we had some design issues that the Jaguars took heat for. There were some teams that stood out as Jaguar success stories and credit goes where it was well deserved, but it was not the best investment of FRC11 time and resources. I look at branches and star in a similar way. It would seem to be an interesting rabbit hole. The recommended design does work so why invest in the alternative? |
Re: Can I branch the CAN to go to two separate places?
Quote:
|
Re: Can I branch the CAN to go to two separate places?
Quote:
|
Re: Can I branch the CAN to go to two separate places?
Quote:
|
Re: Can I branch the CAN to go to two separate places?
Quote:
Time for robot delivery heroics!:D Seriously, not to discourage those who have the time and motivation but there is nothing wrong with the recommended way. So most of those I know that made Jaguars work and other interesting unusual CAN things on an FRC robot (including my Propeller based CAN ESC) leveraged the off season, or knowledge acquired by someone off season, or even knowledge and resources outside of FRC channels. It is wonderful to give that extra dimension, but as the complexity climbs you leave the common denominator behind. FIRST picked a design for the CAN bus that should make everyone work in the 6 week build season and then made sure to build process around it. We should acknowledge potential alternatives exist but not create a situation where the CSA job requires a CAN BERD/BERD in the spare parts kit. |
Re: Can I branch the CAN to go to two separate places?
Quote:
By standard, the maximum recommended stub length is .3 M. Which limits star configurations. Although with the short bus length of your typical FRC robot, you can get away with a lot, but I would stick to the standard. TI has a good application paper on CANBUS here. |
Re: Can I branch the CAN to go to two separate places?
Quote:
Programmers without deep hardware/firmware familiarity and knowledge often face these kind of issues when they do embedded work and robotic systems. It becomes extremely important to have clear disclosure and support. In a way, more CAN devices puts pressure and focus on the system providers to find, resolve and support lest we accumulate risk. I am much more comfortable with how we use CAN now. |
Re: Can I branch the CAN to go to two separate places?
Quote:
It is one of those gotchas that you do have to look for in real life. Which generally made PWM a better choice unless you really needed something that canbus gave you. |
Re: Can I branch the CAN to go to two separate places?
Quote:
|