JMH 18-01-2005 19:49

problems with G22
 
There appears to be a lot of grounds that end at terminal G22. Is this to much load for the terminal?

Please advise us as to whether other ground terminal can be used as well.

Mike Betts 18-01-2005 23:56

Re: problems with G22
 
Quote:

Originally Posted by JMH
There appears to be a lot of grounds that end at terminal G22. Is this to much load for the terminal?

Please advise us as to whether other ground terminal can be used as well.

Please read: http://www.ifirobotics.com/docs/brea...005-revnc0.pdf

If you have further questions, please post and we will try to help.

Al Skierkiewicz 19-01-2005 20:52

Re: problems with G22
 
Quote:

Originally Posted by JMH
There appears to be a lot of grounds that end at terminal G22. Is this to much load for the terminal?

Please advise us as to whether other ground terminal can be used as well.

JMH,
The drawing reads G1-G22 or G1 through G22. These terminals are intended for a single return per terminal. It is best that the device that has it's positive lead connected to a breaker terminal, have it's negative lead connected to the same marked return terminal. i.e. Connect a spike to breaker 15, connect the negative terminal of the spike to G15.