Re: Problems With The Power Distribution Block
At the winter warzone we had all kinds of problems with the block arc-ing and causing our victors to short out. It cost us the quarterfinals there.
|
Re: Problems With The Power Distribution Block
the block is not totally useless. it seves a good purpose, it just has a few "bugs". i agree that it could be a bit lighter, but i dont really mind it. the only problem we had with it was that the main ground wire got pulled out by a divetrain person accidentally tugging on it, which was easily fixed with a screwdriver. overall i dont really care about the block. i just hope FIRST fixes the bugs in the block if they are going to implement it in next years game.
|
Re: Problems With The Power Distribution Block
For other purposes, the block would be amazing. For example, I plan to buy one for a project I'll be doing in my room. It'll be great for that, as I need breaker panels all over the place. However, on a vibrating, moving, slamming robot with only two breaker panels, it's practically useless.
We never had any problems (yet) with the block. One idea we had to meet the rules was to drill holes straight through the block from wire point to wire point, and run the normal wires through the holes. However, we ended up deciding to just wire the thing up in the required manner. |
Re: Problems With The Power Distribution Block
1 Attachment(s)
Quote:
The Rockwell blocks use quasi-parallel clamps to secure the wires. If a wire is not stripped back enough or if the wire is not inserted far enough, the clamp will squeeze/push the wire out of the terminal. If you take a look at the picture (thank you to the Rockwell site) you will see that a wire that is not inserted to the end of the clamp will loosen and fall out. The specification from the Rockwell Catalog for this series (1492-J16) is "Wire Strip Length 0.63 in (16 mm)". The molded-in wire stop correctly positions the wire in the jaws for best termination. Additionally, stranded wire will be forced to change cross section as the clamp pushes down on the wire. This may force teams to check the tightness from time to time. (robot movement will shake wires and make this worse) For these reasons, Loctite is a bad idea on these blocks. Some folks have suggested the use of ferrules over the wire. Debate is still raging but i have some Panduit samples coming in the next week or so to look over. stand by... |
Re: FIRST, if you listen to one suggestion this year, let it be this one
Quote:
-Danny |
Re: Problems With The Power Distribution Block
I know that some manufacturers of similar power distribution blocks (not sure about Rockwell--I haven't spent enough time looking) have spring loaded connectors that may be more suitable for our applications. At least that way the vibration wouldn't loosen the screws and let the wires fall out.
|
Re: Problems With The Power Distribution Block
The spec sheet for the terminal blocks suggests tightening the screws that hold the wires in, to 17 to 35 lb-in torque. That's a lot of torque to apply with a slot screwdriver! Maybe what's needed is to make sure someone with strong hands tightens the connections.
Also double check the wires are stripped the minimum 5/8" length. Having a checklist to double check the tightness of the screws before competition, is a good idea. |
Re: Problems With The Power Distribution Block
Quote:
|
Re: Problems With The Power Distribution Block
Quote:
Make tightening the electrical connections part of your standard preventive maintenance and pre-match checks, just like keeping proper chain tension or making sure the pneumatic release valve is closed. |
Re: Problems With The Power Distribution Block
I am not enamored with the rockwell power distribution block.
The positive end of the block is completely redundant, one can simply route the positive wire through the max-fuse block to the panel for smaller fuses and be done with it. We can do a much lower resistance job for the ground returns with the ground lug from 2004 than we could ever get from the power distribution block. Loctite should not be used on electrical connections, it is not a conductor. There is no substitute for proper torque on all of the electrical screws, and proper stress relief for the wires. The terminal block does need to be tightened to specifications. If you don't have a suitable torque screwdriver, you can do quite well with a wrench attached to a hex drive screw driver, and a small "fishing scale." We have not had problems with bare wire in the power distribution block, but if we have to use this distribution block next year we will certainly use the ferrules. Eugene |
Re: Problems With The Power Distribution Block
All we did was put solder on the wires to stop them from fraying apart, which seemed to be our problem with why they were slipping out. Anyone tried that?
|
Re: Problems With The Power Distribution Block
Quote:
Tinning wire before insertion into a clamp type terminal should not be used. It prevents the wire strands from compressing inside and providing maximum contact area with the terminal. A tinned, stranded wire will act like a solid wire in most cases, usually making the problem worse and raising the series resistance. |