Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: two soleniods controlled by one relay

Alan has described the wiring for this rule.

<R42> Each power-regulating device (speed controller or relay module) shall control one and only one electrical load (motor, actuator or compressor).
Exception: Multiple low-load, pneumatic solenoid valves may be connected to a single relay module. This would allow one relay module to drive multiple pneumatic actions. No other electrical load can be connected to a relay module used in this manner.
The specification on the NI 9472 module is 0.75 amps per output or 6 amps total for the module. If you are looking to just feed two solenoids in parallel from one output and the total current is less than 0.75 amps then that meets specifications. Be prepared to document this should an inspector ask.