Mark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond repute
Re: pressureswitch problem

It certainly sounds like the pressure sensor is doing it's job correctly.

Check your regulator. It could be:
  • set to 90 psi (adjust the knob on it).
  • plumbed backwards (there is an arrow on the back and only the high pressure tube show be going in the port by the back of the arrow).