Travis,
You might want to focus on the compressor. When it is intermittent, is the DSC LED for that relay channel steady or intermittent? If the former, then software is probably not at fault. If the latter, then the DSC is being commanded to intermittently run the compressor by the CRIO and software is highly suspected.
If the above indicates software is OK, you might want to temporarily disconnect the spike to the compressor. Does the 550 operate smoothly? If so, you may have a circular path somehow in your frame...
Good Luck,
Mike