Gdeaver has a reputation beyond reputeGdeaver has a reputation beyond reputeGdeaver has a reputation beyond reputeGdeaver has a reputation beyond reputeGdeaver has a reputation beyond reputeGdeaver has a reputation beyond reputeGdeaver has a reputation beyond reputeGdeaver has a reputation beyond reputeGdeaver has a reputation beyond reputeGdeaver has a reputation beyond reputeGdeaver has a reputation beyond repute
Re: Analog break out problem.

I would have to confirm the revision of the board but it is this years break out. The big problem with noise was the break out with the vishay sensors but some with IR's. The 1k pull ups were added. no effect on the noise. I believe their main purpose is to give a clean high signal for diagnostics. So this years break out 5 vishays and noise. One 10 uf electrolytic cap on the + and - and it's clean. Is this just our board or is it a deeper problem? Any other reports. The fix is simple but frustrating till it was found.