Jon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond repute
Re: Disabling PWM outputs w/out disabling entire bot.

Quote:
Originally Posted by Mark McLeod View Post
The pressure switch isn't rated for the peak current draw of the compressor as it starts up.
It's only rated for 5 amps.
Very true (our mechanical team blew a switch doing exactly that one summer... they never asked the electrical team to hook it up for them or we would have done it right). However, the switch can be used as signal inputs directly into a relay - then the relay handles the big current load, while the switch needs a much smaller current to activate the relay.