Temporarily, you could either double up wires coming out of a breaker, or wire your motor to a smaller breaker. You should still have some 20A and 30A breakers left.
|
This is not legal. R43, Part A states:
Quote:
|
Each speed controller branch circuit must be protected by one and only one 20-amp, 30-amp, or 40-amp circuit breaker on the PD Board (from the KOP or identical equivalent). No other electrical load can be connected to the breaker supplying this circuit.
|
Each speed controller needs its own individual branch circuit.
The easiest solution is going to be to obtain additional circuit breakers:
http://www.andymark.com/Power-s/263.htm
You can attach Jaguars to 20 or 30 Amp circuit breakers as well... for a window motor, 20A works just fine - we've never had an issue doing that, and we've put some amazing stress on the window motors in the past.