Tristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond repute
Re: 2 Signal lights?

Quote:
Originally Posted by BioWolf View Post
wait.
quick question.
so i cant find the minimum AWG for the RSL. can anyone help me?
Q&A said there isn't any (2012 question 386).

Use what's recommended by the manufacturer for the 855PB-B12ME522 panel signal device: "up to 2.5 mm2 (14 AWG)". I'd avoid going smaller than 30 AWG for solid wire, or 24 AWG for stranded wire, mostly for ease of use; it only draws 60 mA, so capacity isn't a big issue.