Quote:
Originally Posted by Ether
Using a custom PWM signal generator, I have run the Vic888 with periods from 5ms to 20ms, and with pulse widths from .5ms to 2.5ms with no problems. I believe I did the same with the Talon, also with no problems.
[edit]
Just calibrated an 888 driving a 500 ohm resistive load. Calibrated to 2.000 ms max, 1.000 ms min, and 1.500 ms neutral. Then measured, and got 1.990 ms max, 1.021 ms min, and deadband from 1.482 ms to 1.523 ms
[/edit]
|
The problem that the comment that Tom is referring to was finding what values work best with factory default calibration, and with the Victor 884, it varied unit to unit.