Kevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond repute
Send a message via AIM to Kevin Sevcik Send a message via Yahoo to Kevin Sevcik
Re: Why not to shift?

Quote:
Originally Posted by DampRobot View Post
For a team with 6 drive motors (for example, let's say a 775 and two CIMs), how fast would the robot be traction limited at? I would assume if a 2 CIM drive is traction limited at 6fps, then with a 775, the traction limited single speed gearing allow for a top speed around 8fps. Could you, theoretically, just throw power onto the drive until you were traction limited at, say 13fps?

On a related thread, how many motors can you give a drivetrain while still drawing less current than the main breaker will pop at? An unsophisticated analysis says that even 4 CIMs drawing 40 amps (ie, accelerating from a stop) will pop the 120 amp main breaker. Is the limit on the number of motors which can reasonably be put in the drive dictated by the main breaker?
Actually, those circuit breakers won't ever trip at the rated current. Take a look at the attached datasheet to get a feel for the trip times. According to the data sheet, at 200% rated current, they should take at least 10 seconds to trip. It looks like about 20 seconds at 150%. That's assuming no heavy bumps, of course.

So based off that, on a 4CIM drivetrain, you'd likely fault out jaguars or trip your 40A breakers before you tripped the main 120A breaker.
Attached Files