Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: Using CIMs at 30 amps?

The breaker rules are written to protect wire and nothing else. Should a branch circuit using #12 wire (or larger) short for any reason, the wire feeding the branch will not melt or catch on fire with a 40 amp (or smaller) breaker. Circuit breakers do not limit the current flow they simply open when the specified trip current is exceeded. However, a six CIM shooter sounds like something I would like to see work. It scares me but I still would like to see it.