In my experience, if only one port is working or if you're having port issues, it's got something to do with the Digital Sidecar. My team had a similar issue, and it turned out to be that the DSC wasn't getting enough power.
So, basic troubleshooting for that would be remove the ribbon cable that connects the Digital Sidecar to the Digital Breakout, and check if all 3 lights are lit (BAT 5V 6V) if they're still lit, then that means you've got good power. If one of them isn't lit, make sure that your DSC is connected correctly to the Power Distribution board as seen
here.
That's what I'd start with. Hope it helps