Daniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond repute
Send a message via MSN to Daniel_LaFleur
Re: Victor connect to 30 A instead of 40 A

Quote:
Originally Posted by FrankJ View Post
The idea that the breaker is sized just to protect the wire is facilities logic. When you size breakers or other over current devices on a piece of equipment, like a robot, you size them for the protection of the load. You size the wire to suit.

A smaller breaker won't hurt your victor, it might save your motor.
Sorry, FrankJ, but I respectfully disagree.

A breaker or fuse is no where near fast enough to protect a load from overcurrent (look at the trip specs).It is, instead, there to protect the rest of the wiring from an overcurrent event once a electrical failure has occurred. Thus, you size the wire to suit the load and you size the fuse/breaker to protect the wiring.