IndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond repute
Re: Victor connect to 30 A instead of 40 A

Quote:
Originally Posted by Daniel_LaFleur View Post
Sorry, FrankJ, but I respectfully disagree.

A breaker or fuse is no where near fast enough to protect a load from overcurrent (look at the trip specs).It is, instead, there to protect the rest of the wiring from an overcurrent event once a electrical failure has occurred. Thus, you size the wire to suit the load and you size the fuse/breaker to protect the wiring.
Daniel, a breaker is there to protect load and the wiring. If you use 12ga wire instead of 14ga with a 30a breaker you are actually adding a level of security. The wire will be much less likely to be damaged if you have a load that trips the breaker.
__________________
"Champions are champions not because they do anything extraordinary but because they do the ordinary things better than anyone else." —Chuck Knoll


2015 Indianapolis District Winner
2014 Boilermaker Regional Industrial Design Award
2013 Smoky Mountain Regional Industrial Design Award
2012 Boilermaker Engineering Excellence Award
2010 Boilermaker Rockwell Innovation in Control Award.
2009 Buckeye J&J Gracious Professionalism Award
2009 Boilermaker J&J Gracious Professionalism Award
2008 Boilermaker J&J Gracious Professionalism Award
2007 St Louis Regional Winners