Daniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond repute
Send a message via MSN to Daniel_LaFleur
Re: Victor connect to 30 A instead of 40 A

Quote:
Originally Posted by seg9585 View Post
What's "not quite right"? I don't know about you, but I choose my wire based on the motor and its associated load, and select a breaker current limit accordingly. You really do it the other way around?

<SNIP>
My previous statement was, in effect, you choose the wire size by the current draw of the load (motor, etc.) and then you choose the breaker by the wire size.

Breakers (and fuses) do not limit current. they open the circuit when the bimetallic surfaces get too hot. In the case of auto-resetting breakers they then close the circuit when the bimetallic surfaces cool.

Again, size the breaker (or fuse) for the wires connected to it.