Thread: Bad 40A Breaker
View Single Post
  #3   Spotlight this post!  
Unread 18-02-2003, 21:33
Richard Wallace's Avatar
Richard Wallace Richard Wallace is offline
I live for the details.
FRC #3620 (Average Joes)
Team Role: Engineer
 
Join Date: Jan 2003
Rookie Year: 1996
Location: Southwestern Michigan
Posts: 3,658
Richard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond repute
More on the Bad 40A Breaker

I got some time to test the bad breaker today. Connected it to a regulated laboratory power supply, Sorensen model DCS 20-150, in regulated current mode. Increased the current slowly and saw nothing unexpected until it reached about 30A. At that point its started switching on and off very rapidly. This is consistent with the behavior observed when the bad relay was in our robot.

Seems that we damaged it somehow, or maybe it was bad from the start.

Again, has anyone seen similar 40A breaker behavior?
__________________
Richard Wallace

Mentor since 2011 for FRC 3620 Average Joes (St. Joseph, Michigan)
Mentor 2002-10 for FRC 931 Perpetual Chaos (St. Louis, Missouri)
since 2003

I believe in intuition and inspiration. Imagination is more important than knowledge. For knowledge is limited, whereas imagination embraces the entire world, stimulating progress, giving birth to evolution. It is, strictly speaking, a real factor in scientific research.
(Cosmic Religion : With Other Opinions and Aphorisms (1931) by Albert Einstein, p. 97)