While inspecting at the Sacramento regional, I came across a team that had this issue, or one similar to it.
Their compressor would run whenever the robot was powered on. They said "It has always done that.", which unnerved me a bit.
Long story short, they had the Spike relay for the compressor plugged into a PWM port with the jumper in place for use with a servo.
The jumper provided +6vdc to the center wire, thus telling the Spike to go into forward at all times.
So, check the wiring.