I have a few questions about the new hardware.
Does the CAN bus support multiple pneumatics modules?
Are the 12 volt connectors with the 20/10 amp fuses on the PDP regulated? (I don't think so, but I'm not sure)
Do the compressor, solenoids, and voltage regulator module, which powers cameras, custom circuits, and the radio share the same single 20 amp fuse? If this trips (because of compressor current spikes or short anywhere) does this mean radio power is lost?
|
Team 358's website is an awesome resource for the beta test. They really have everything.
From reading their description, you're right about how it works.
Quote:
|
(2) dedicated power for Pneumatics Module and/or Voltage Regulator w/20a fuse
|
I agree that putting the radio, the most critical component of the control system, on a non-resetting fuse that is shared with many other loads is a silly idea. Starting a compressor when the battery is very low often trips the spike's fuse, and in addition, we are also powering 8 solenoid valves (less than .25 amps for all 8 channels going at the same time) and over 3.5 amps (@ 12 volts) from the VRM.