Oblarg has a reputation beyond reputeOblarg has a reputation beyond reputeOblarg has a reputation beyond reputeOblarg has a reputation beyond reputeOblarg has a reputation beyond reputeOblarg has a reputation beyond reputeOblarg has a reputation beyond reputeOblarg has a reputation beyond reputeOblarg has a reputation beyond reputeOblarg has a reputation beyond reputeOblarg has a reputation beyond repute
Re: Needing help with the double solenoid

Quote:
Originally Posted by Jesus Perea View Post
70 PSI.
And also we change the solenoid and it was the same problem
Ok.

I notice in your code that it seems you're trying to control the double solenoid using two single solenoid controllers.

This is bad practice, since there are states possible for two single solenoids that are not possible for a double solenoid (i.e. both open or both closed). If you attempt to put the solenoid into one of these states, it probably could cause problems/not work (full disclosure: this is not a mistake I have ever made myself, so I do not know exactly what happens if you do it).

Try using the double solenoid option instead of the single and see what happens.