protoserge has a reputation beyond reputeprotoserge has a reputation beyond reputeprotoserge has a reputation beyond reputeprotoserge has a reputation beyond reputeprotoserge has a reputation beyond reputeprotoserge has a reputation beyond reputeprotoserge has a reputation beyond reputeprotoserge has a reputation beyond reputeprotoserge has a reputation beyond reputeprotoserge has a reputation beyond reputeprotoserge has a reputation beyond repute
Re: New benchtop mill

Quote:
Originally Posted by RoboChair View Post
If you have a 10A breaker, there are no problems on the part of the 14g wire upgrading it to a 15A breaker. A 2 HP Bridgeport at peak amperage being run via a VFD is 12.5A @120V even with efficiency losses you would have to be pushing that mill very hard to hit 15A.

12g can be bumped to 20A
10g can be bumped to 30A
I thought you were saying to change a 15A breaker to 20A. That would be a terrible idea. I have seen it done before and had conduit that was hot to the touch. Sorry for the confusion on my part.