Re: Ports changed independently?

Quote:
Originally Posted by tr6scott View Post
Check the can buss for issues, look for retry counts, (I think the are on the same status page, going from memory) make sure you have the can wired correctly, with terminating resistors at each end, and daisy chained through the devices.

When Setting device id's make sure you use the "Flash LED" command to identify the correct talon srx before setting the id and buss number. Quite common to setting the id to another SRX than the one you wanted.
Quote:
Originally Posted by GeeTwo View Post
As the symptoms don't make much sense for PWM control, I'm presuming that you're using Talon SRXs controlled through CAN.

What did you do with the
?

Best guess:

It sounds like the Talon SRXs were never given addresses, or given duplicate addresses. The directions to detect and correct this is given in section 2.2 (pages 16 and 17) of the Talon SRX Software Reference Manual. Note that it is necessary to refresh the browser after changing the address; failure to do this caused us some unnecessary confusion the first time we did it. We now do a refresh following each assignment; possibly overkill, but better than confusion.
Another thing that happens, is that it shows that a talon srx is a pdb and sometimes even a vrm, which gets me even more confused (Image added as example)

http://imgur.com/a/AgTjm