Another caution is that piloted pneumatic solenoids like FRC teams typically use, must have a certain minimal air pressure to work reliably or at all.
Usually this minimum pressure will be between 20 and 25psi. It should be in the manufacturers notes.
Pressure dips in the low-pressure regulated system may also drop you below that minimum momentarily, so activating one set of solenoids may momentarily disrupt the operation of another set.
Just test all possible conditions and firing combinations so you are aware.