Re: Climber help: thermal breakers.

Quote:
Originally Posted by RoboChair View Post
Risk of the 67 Amps through the snap action breakers, someone else will need to weigh in on that. Personal feeling is not of much concern because they reset.

Main breaker: 1% concern. You can dump 500 amps through it for over a second if I recall correctly. 140 amps can draw for well over a minute. Who has the chart?
http://files.andymark.com/PDFs/am-0282_data_sheet.pdf

See the chart on the bottom right of the first page. You can go for ~5s at ~480 amps (120 * 400%).

Never worked with overloading snap actions before, but the chart on their data sheet shows that it should be ok to run 67 amps through one (167.5% of the rated current, which the data sheets say could be done for about .. 5s?

http://files.andymark.com/MX5SpecSheet.pdf

Last edited by ollien : Yesterday at 03:19. Reason: Snap Action Info