dez250 has a reputation beyond reputedez250 has a reputation beyond reputedez250 has a reputation beyond reputedez250 has a reputation beyond reputedez250 has a reputation beyond reputedez250 has a reputation beyond reputedez250 has a reputation beyond reputedez250 has a reputation beyond reputedez250 has a reputation beyond reputedez250 has a reputation beyond reputedez250 has a reputation beyond repute
Send a message via AIM to dez250
Re: wiring solenoids

Quote:
Originally Posted by Charley
Is there a maximum PWM wire connecting the solenoid to the spike? We just fried ours, and want to step it up : ).

Thanks,
Charley.
If your talking about how many solenoids can be wired to each spike, that number is one. All though (as the 2004 wiring diagram shows) you can wire upto 3 solenoids each through their own spike to 1; 30 amp fuse on the breaker.