Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: problems with G22

Quote:
Originally Posted by JMH
There appears to be a lot of grounds that end at terminal G22. Is this to much load for the terminal?

Please advise us as to whether other ground terminal can be used as well.
JMH,
The drawing reads G1-G22 or G1 through G22. These terminals are intended for a single return per terminal. It is best that the device that has it's positive lead connected to a breaker terminal, have it's negative lead connected to the same marked return terminal. i.e. Connect a spike to breaker 15, connect the negative terminal of the spike to G15.