Re: Bad Breaker Panel?
Are you mounting the electronics to metal? The mounting screws of the speed controllers come dangerously close to the wire terminal connections.
Are all of the wires disconnected when you are measuring the resistance? If not, you may be measuring a load.
To test the breaker panel, I would remove all breakers, disconnect all of the wires, apply power and measure the ouitputs. You should get no voltage on the outputs until you insert the breakers.
|