Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: Door Motor Wire gage

Quote:
Originally Posted by WebWader125
This year's rules only specify #12 for the 40 amp breaker, and 14 for the 30 amp breaker.
Yes,
But don't forget the "minimum wire guage" is not the best for your purposes. My recommendation is #10 for Chalupas, FP, Drills or anything that could be run from a 30 or 40 amp breaker.
__________________
Good Luck All. Learn something new, everyday!
Al