Nate Laverdure has a reputation beyond reputeNate Laverdure has a reputation beyond reputeNate Laverdure has a reputation beyond reputeNate Laverdure has a reputation beyond reputeNate Laverdure has a reputation beyond reputeNate Laverdure has a reputation beyond reputeNate Laverdure has a reputation beyond reputeNate Laverdure has a reputation beyond reputeNate Laverdure has a reputation beyond reputeNate Laverdure has a reputation beyond reputeNate Laverdure has a reputation beyond repute
Re: Air Compressor Wireing question

The pressure switch is not rated to 12 volts, so it must be wired through the robot controller.

<R103> The Nason pressure switch must be connected to the output end of one of the Clippard
tanks to sense the tank’s pressure. The two wires from the pressure switch must be
connected directly to a digital input and ground terminal on the Robot Controller, and the
controller must be programmed to sense the state of the switch and operate the relay
module that powers the compressor
. The Parker pressure vent valve must be connected to
a Clippard tank such that, when manually operated, it will vent to the atmosphere to relieve
any stored pressure. The valve must be placed on the ROBOT so that it is visible and
accessible.