Mike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond repute
Re: Solenoids + 20A breakers.

Joel,

From an electrical engineering perspective, wiring multiple Spikes to one 20A CB is OK as long as the total load is less than 20A. However, the 2007 Robot Power Distribution Diagram shows individual CBs to each Spike...

I would like to see someone post this question to the FIRST Q&A for a ruling clarification.

Regards,

Mike