Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: problem with speed controller

To go along with the original problem and folllowing up on Ricky's post...
A flashing red indicator is likely from the controller getting a full reverse command and the breaker tripping. There is no flashing red programmed into the controller. It sounds like the motor wiring is shorted. That way high currents are developed when the controller is told to apply power to the motor.