Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: Maxi Block Issue

Paul,
The wire is protected by the breaker sizing. If the motor stalls, the breaker must trip to prevent the wire from going incandescent.
The breakers realistically have a trip charachteristic that allows them to pass more than 600% over current for a short period of time and can pass almost 150% current indefinetely. As strange as it sounds, you can put a 40 amp breaker on a motor that has a 20 amp stall current as long as the wire is #12 AWG or larger. I wouldn't do it, but you could.
BTW, In looking at spec sheets for both the Kayang and Taigene motors, there appears to be an internal, temperature controlled, breaker on both motors.