Dave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond repute
Re: Powering the IR detector from +5V instead of 7+ V.

Quote:
Originally Posted by Dad1279 View Post
However <R55> reads as follows:
.....
• The Robot Controller power feed must be protected with a 20A circuit breaker. No other electrical load can be connected to this breaker.
......
• Power feeds to custom circuits and additional electronics must be protected with a 20A circuit breaker.
......
In past years, R55 has been interpreted to mean that *if* you feed a custom circuit 12v, then it must be from a 20A breaker. However, custom circuits that were powered from the RC's 5v line were specifically allowed (and I asked a Q&A to make sure):
http://forums.usfirst.org/showthread.php?t=1518

Now, there's the standard catch about "last year is not this year", but when the rule in question does not change at all from 2007 to 2008, and this is how it was interpreted in 2007, then I don't see why anything would be different this year.