I missed that R64 -- we are not using that module or it's breakout. So we have to have it on there anyway??? Or does the rule imply that if we're using it, then it must be in that slot?
Either way, we could've shuffled the other modules so the digital sidecar clears.
|
Yes, you must have the analog module in slot 1 with a 12-volt supply connected from a 20 amp breaker on the power distritution and the analog breakout's jumper set to read battery voltage.
No, you can not shuffle modules. They must be in the defined slots. Mandatory analog in slot 1 (with battery monitor jumper) and digital in slot 4 (with attached sidecar connected to Robot Signal Light). Optional analog in slot 2, digital in slot 6, and pneumatic in slot 8.