samir13k has a brilliant futuresamir13k has a brilliant futuresamir13k has a brilliant futuresamir13k has a brilliant futuresamir13k has a brilliant futuresamir13k has a brilliant futuresamir13k has a brilliant futuresamir13k has a brilliant futuresamir13k has a brilliant futuresamir13k has a brilliant futuresamir13k has a brilliant future
Send a message via AIM to samir13k Send a message via MSN to samir13k
Re: 5 amp circuit breakers

Quote:
Originally Posted by Joe Ross View Post
Don't confuse the control system manual with the rules. The control system manual tells you how things can be connected and used, the rules (specifically section 8) tell you how things must be connected for FRC.

<R46C> says that the digital sidecar must be protected by a 20amp breaker. <R47C> says that everything protected by a 20amp breaker must use 18awg wire or larger.

If you were doing this for fun, you could use a 5amp breaker and 22awg wire safely. As you pointed out, it isn't safe to use a 20amp breaker and 22awg wire.
Joe is correct, look at the rulebook first. especially the sections he has quoted above. It is a good idea for your electrical person to print off the few pages with wire gauges and breaker requirements and keep them at his workstation while wiring.