Quote:
Originally Posted by jsasaki
Im sorry but im not exactly getting this but from what i've been hearing/reading the pneumatic bumper is connected to the 24v source on the distribution board (2 left over leads on the WAGO connector that connects the cRio to the Distribution board) and then the two ends of the solenoid being connected to the bumper right? So if this is right that means were gonna have to use 2010 and only the 2010 festo valves hence the 2008 and 2009 SMC and Festo valves are not going to have the right amount of voltage thus not working right???? This years pneumatics are complicated  we should have sticked with the old SMC and Festo solenoid
thanks for you help
|
That is correct, you could only power the 2010 Kit solenoid valve off of the 24V Solenoid Breakout (or any purchased 24V solenoid valves that meets the requirements of the rules).
You can use an additional Solenoid Breakout board connected to a 20A breaker to power 12V solenoids on the same robot. You could also use one or more Spike Relays to power 12V solenoids.