Re: Compressor won't start

Quote:
Originally Posted by 1075guy View Post
The compressor WILL NOT RUN without the pressure switch connected, this is because the switch is a normally closed contact, that goes open when its reached pressure.

I didn't check our pressure switch, but it's odd that everything works. The compressor turns on and off as expected, confirmed by the pressure gauge, and the compressor runs when the switch is not wired. That's why I thought the switch must be normally open, but reading the spec, it is normally closed. We're declaring the standard Compressor object and using m_compressor->Start(). Maybe the floating cRIO digital input is picking up noise and sensing it as a logic low, turning on the compressor?

Last edited by oddjob : 19-02-2010 at 08:26.