Ether has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond repute
Re: Compressor not stopping at 120psi

Quote:
Originally Posted by robself705 View Post
If the controller is on: use the voltmeter to measure 0 or 5v across the switch.
Yes, use the voltmeter setting, not the ohmmeter.


Quote:
Originally Posted by robself705 View Post
If 5v the switch is closed (115 psi) if 0v the switch is open ( less than 95 psi).
It's the other way around. 5V means the switch is open; 0V means the switch is closed.


~