EricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond repute
Send a message via AIM to EricVanWyk
Re: Multiplex Festo Valves

You can actually use 2 solenoid breakouts, this was addressed in an update. Up to one of these can be 24V.

Al is (as usual) correct. You can not drive >8 24V valves with the 2010 control system. It is both illegal and there is not enough headroom in the 24V supply to do so.